T12 AND T8 ballast? Or does it have to be one or the other?

Paperdesk

Newly Enlightened
Joined
Dec 20, 2005
Messages
50
Hi! I'm really confused about some light fixtures I have. I bought the cheap shop lights Walmart sells. I didn't really pay any attention to what the box said, put T12 bulbs in, and threw the boxes away.

Then I got to thinking that maybe the fixtures had T8 ballasts, so I looked up the model number, and found this: http://www.lightsofamerica.com/Products/8045E.aspx

The product description says it can operate either T8 or T12 bulbs. Is it possible that for $10 you could buy a light with a ballast that is well suited for both types? I figured it was actually designed for T12 but T8 still works (with more rapid loss of bulb life).

I'd rather run T8's, but only if the fixture was truly designed for that!

Do some ballasts work well for both T8 and T12?

Thanks!

Ted
 

aruzinsky

Newly Enlightened
Joined
May 12, 2010
Messages
15
It was designed to operate T8 well because the power rating is about 32 watts/bulb. It operates T12 at substantially less than than the bulb rating of 40 watts. Your reference doesn't specify whether the fixture uses instant or rapid start ballasts. You should know that most, if not all, T12 bulbs are NOT designed for use with instant start ballasts. That doesn't stop ballast manufacturers from making instant start ballasts for T12 bulbs, but using instant start ballasts voids T12 warranties, not that I would worry.
 

Paperdesk

Newly Enlightened
Joined
Dec 20, 2005
Messages
50
So these lights will operate either bulb type, but the T8's much more efficiently, right?

This brings up an interesting question. I don't know how if these fixtures have instant or rapid start ballasts, but they do say they have "cold start" ballasts.

I ran T12 bulbs in these fixtures for a while, but put T8 bulbs in to see if they would work. They worked well for several days, but then a couple of the fixtures quit working. I checked to make sure the bulbs were seated properly and still they didn't work. However, when I unplugged the fixtures, and plugged them back in they started working again. This happened a number of times, though sometimes I have to unplug several times before they will kick on again. I put T12 bulbs back in, and they consistently worked fine. Strange! Maybe this has something to do with the instant/rapid start ballast issue?
 

jhellwig

Newly Enlightened
Joined
Nov 23, 2008
Messages
182
Location
Ottumwa, Ia
It was designed to operate T8 well because the power rating is about 32 watts/bulb. It operates T12 at substantially less than than the bulb rating of 40 watts.

4' T12 bulbs are rated for 34watts. Energy saving and all that bs.

Fullam (I think it the name) is one manyfacture of ballast that have a wide range of bulbs that they can operate. The basicly give you a maximum wattage that the ballast can handle.
 

aruzinsky

Newly Enlightened
Joined
May 12, 2010
Messages
15
4' T12 bulbs are rated for 34watts. Energy saving and all that bs.

Fullam (I think it the name) is one manyfacture of ballast that have a wide range of bulbs that they can operate. The basicly give you a maximum wattage that the ballast can handle.

No, SOME T12 bulbs are rated for 34watts; most typically 4 ft. T12 bulbs are 40 watts. See http://en.wikipedia.org/wiki/Fluorescent_lamp_formats .
 

aruzinsky

Newly Enlightened
Joined
May 12, 2010
Messages
15
So these lights will operate either bulb type, but the T8's much more efficiently, right?

If the ballasts are instant start, it is rumored that the average life of the T12 bulb will be shorter than advertised and there is a safety issue because the ends of failed T12 bulbs will become very hot. T12 bulbss are usually less efficient than T8s for other reasons.

This brings up an interesting question. I don't know how if these fixtures have instant or rapid start ballasts, but they do say they have "cold start" ballasts.

You should be able to see whether the lights come on instantly or not.

I ran T12 bulbs in these fixtures for a while, but put T8 bulbs in to see if they would work. They worked well for several days, but then a couple of the fixtures quit working. I checked to make sure the bulbs were seated properly and still they didn't work. However, when I unplugged the fixtures, and plugged them back in they started working again. This happened a number of times, though sometimes I have to unplug several times before they will kick on again. I put T12 bulbs back in, and they consistently worked fine. Strange! Maybe this has something to do with the instant/rapid start ballast issue?

I doubt it. I have used American Fluorescent 234SLESW Shoplights (instant on) without problems. Sometimes they are on sale at Menards for around $10-$15.
 

oldwesty4ever

Newly Enlightened
Joined
May 24, 2010
Messages
110
If it is designed for either T8 or T12, using either wont affect the ballast but as others said if the fixture lights the tubes instantly its hard on the T12s. I also think the fixture will underdrive T12s by driving 40w rated lamps at 32w, so they will be slightly dimmer than the T8s in this fixture.
 

jhellwig

Newly Enlightened
Joined
Nov 23, 2008
Messages
182
Location
Ottumwa, Ia
No, MOST t12 4 foot bulbs are rated for 34 watts. When the bulbs originaly came out they were 40 watt. When the first wave of energy regulation came out in the day they went to 34 watt. Yes you can still buy 40 watt bulbs but they are the more specialized bulbs and bulbs aimed at the every day consumer that only comprehends bigger numbers and shiney packaging. If you buy the cheap normal warm white or cool white bulbs they will be 34 watt. Go to an electical supply house and the very big majority of bulbs they have are gonna be the lower wattage ones.

If you buy "shop light" bulbs they are rated for 25 watt.
 

Paperdesk

Newly Enlightened
Joined
Dec 20, 2005
Messages
50
Very interesting! My lights come on right away, so I guess they're instant start. Still seems strange that some fixtures will run the T12 bulbs but not the T8 bulbs, and others that were bought at the same time and are the same model, will run the T8's just fine. Interestingly enough, I found a T10 bulb in with my other bulbs, I don't even know where that one came from!

I'll think for now I'll run T8 bulbs in as many of the fixtures as I can, and run T12 in those that won't power the T12's.

Ted
 

aruzinsky

Newly Enlightened
Joined
May 12, 2010
Messages
15
Very interesting! My lights come on right away, so I guess they're instant start. Still seems strange that some fixtures will run the T12 bulbs but not the T8 bulbs, and others that were bought at the same time and are the same model, will run the T8's just fine. Interestingly enough, I found a T10 bulb in with my other bulbs, I don't even know where that one came from!

I'll think for now I'll run T8 bulbs in as many of the fixtures as I can, and run T12 in those that won't power the T12's.

Ted

What are the wattage ratings written on your T12 bulbs?
 

aruzinsky

Newly Enlightened
Joined
May 12, 2010
Messages
15
No, MOST t12 4 foot bulbs are rated for 34 watts. When the bulbs originaly came out they were 40 watt. When the first wave of energy regulation came out in the day they went to 34 watt. Yes you can still buy 40 watt bulbs but they are the more specialized bulbs and bulbs aimed at the every day consumer that only comprehends bigger numbers and shiney packaging. If you buy the cheap normal warm white or cool white bulbs they will be 34 watt. Go to an electical supply house and the very big majority of bulbs they have are gonna be the lower wattage ones.

If you buy "shop light" bulbs they are rated for 25 watt.

And, where, besides Iowa (population 3,007,856 ), is this "energy regulation?" Look at the 40 watt T12 bulbs advertised by Menards in Illinois (population 12,910,409) Chicago area:
MenardsFluorescent001.jpg

In fact, I have never seen less than a 40 watt 4' T12 advertised here.
 

Paperdesk

Newly Enlightened
Joined
Dec 20, 2005
Messages
50
My T12 bulbs all say 40 watt. I just bought a bunch more from Walmart and they also say 40 watt. Maybe in CA or other states they only sell 34 watt or something? I'm in WA.
 

aruzinsky

Newly Enlightened
Joined
May 12, 2010
Messages
15

jhellwig

Newly Enlightened
Joined
Nov 23, 2008
Messages
182
Location
Ottumwa, Ia
Shiney consumer oriented packaging special purpouse blaa blaa blaa excuse me for being an electrician for and not doing much residential never seen a 40 watt outside of stuff from 1955 yada yada yada or whatever junk the homeowner bought from menards flippity floopity floop changed out a mind numbing amount of bulbs and ballast in industrial and commercial facilities and never run across 40 watt bulbs.............


On another note I just read through the ge light bulb catalog and see that they still make 75 watt 8' bi-pin bulbs.......


Can I go ahead and say that those cheap shoplites use cheap ballasts that don't last long anyways so don't lose any sleep over what bulbs you put in them or is anyone going to object to that observation?
 
Last edited:

yuandrew

Flashlight Enthusiast
Joined
Apr 12, 2003
Messages
1,323
Location
Chino Hills, CA
Take apart the fixture and see if it has 1 or 2 little boxes with wires coming out tucked in the ends between the lamp sockets. If so, it's likely based on the "resi-tronic" ballast which are pretty terrible. They are nothing more than just a bunch of capacitors) and are known to burn lamps out rather quickly (sometimes within as little as 2 months). If you pay close attention, you'll notice that one end of the tube gets blackened rather quickly.

I've experimented with running T8 tubes on T12 ballasts in the past and its pretty picky. My best result was with an old Robertson S40B Preheat ballast (the type requiring a starter). Most residential rapid-start ballast I tried don't fully light the tube up with the exception of a single lamp Advanced Mark III although that one blackened the tube ends rather quickly.

Keep in mind not all T12 ballast will act nicely with T8 tubes. Some old GE-Magnatek-Universal ballast do not like anything other than true 40 watt tubes. Even the 34 watt "energy saver" tubes will case them to overheat and eventually burn out.
 

aruzinsky

Newly Enlightened
Joined
May 12, 2010
Messages
15
You can easily upgrade the ballasts in some cheap T12 shoplight fixtures. I replaced old magnetic ballasts with this instant start ballast, http://ballastwise.com/item.asp?PID=3&FID=14&level=1 . I have been using one fixture in my kitchen without problem for over 6 months where it is turned on/off about 20 times per day. (turning on/off frequently is supposed to be hard on bulb life)

Also, you should be aware that overdriving fluorescent bulbs is a common practice among those who grow plants under fluorescent light. Here is a link on overdriving:

http://reocities.com/heartland/pines/7557/overdrv1.html
 

aruzinsky

Newly Enlightened
Joined
May 12, 2010
Messages
15
Take apart the fixture and see if it has 1 or 2 little boxes with wires coming out tucked in the ends between the lamp sockets. If so, it's likely based on the "resi-tronic" ballast which are pretty terrible. They are nothing more than just a bunch of capacitors) and are known to burn lamps out rather quickly (sometimes within as little as 2 months). If you pay close attention, you'll notice that one end of the tube gets blackened rather quickly.

I've experimented with running T8 tubes on T12 ballasts in the past and its pretty picky. My best result was with an old Robertson S40B Preheat ballast (the type requiring a starter). Most residential rapid-start ballast I tried don't fully light the tube up with the exception of a single lamp Advanced Mark III although that one blackened the tube ends rather quickly.

Keep in mind not all T12 ballast will act nicely with T8 tubes. Some old GE-Magnatek-Universal ballast do not like anything other than true 40 watt tubes. Even the 34 watt "energy saver" tubes will case them to overheat and eventually burn out.

I am under the impression that more people run T12 on T8 electronic ballasts instead of vice versa. I have done this also with overdiving.
 

Bright+

Newly Enlightened
Joined
Dec 5, 2008
Messages
170
T12s are designed for 0.43A. T8s are 0.27A. When they're in operating state, T8s have higher voltage (this is different from open circuit voltage, which is the ignition voltage).

T8 ballasts usually allow the use of 2 to 4' lamps and they do so by being a current source and voltage changes accordingly.
So, when you operate T12s in a T8 fixture, they'll run at lower power than T8s. The other way around, it may malfunction(flash or not start) or the ballast can burn out from operating at higher power than it was designed for.

If you slap in cheap 34W T12 bulbs you will get crappy light as they are 60 CRI. Good T8s have CRI of 85 as do premium T12s, but the latter costs more, so you might as well just get T8.

Get GE Sunshine T8 they have at Lowe's if you want "cool" 5000K or Philips Soft White T8 if you want warmer 3000K.
 

call0031

Newly Enlightened
Joined
Aug 3, 2014
Messages
1
So these lights will operate either bulb type, but the T8's much more efficiently, right?

This brings up an interesting question. I don't know how if these fixtures have instant or rapid start ballasts, but they do say they have "cold start" ballasts.

I ran T12 bulbs in these fixtures for a while, but put T8 bulbs in to see if they would work. They worked well for several days, but then a couple of the fixtures quit working. I checked to make sure the bulbs were seated properly and still they didn't work. However, when I unplugged the fixtures, and plugged them back in they started working again. This happened a number of times, though sometimes I have to unplug several times before they will kick on again. I put T12 bulbs back in, and they consistently worked fine. Strange! Maybe this has something to do with the instant/rapid start ballast issue?

As I read the following website, you could burn your house down if you put the wrong wattage T-12 in a T-8 fixture. Apparently this is a common cause of fires. It says "You should not install 40 watt lamps in a fixture running a ballast meant for 34 watt lamps." If you have used T-12s in a T-8 fuxture and then are having problems I would definitely be concerned about what happened inside your ballast. See http://www.envirolightusa.com/articles/4.html
 

Bill123

Newly Enlightened
Joined
Sep 22, 2014
Messages
1
Hi! I'm really confused about some light fixtures I have. I bought the cheap shop lights Walmart sells. I didn't really pay any attention to what the box said, put T12 bulbs in, and threw the boxes away.

Then I got to thinking that maybe the fixtures had T8 ballasts, so I looked up the model number, and found this: http://www.lightsofamerica.com/Products/8045E.aspx

The product description says it can operate either T8 or T12 bulbs. Is it possible that for $10 you could buy a light with a ballast that is well suited for both types? I figured it was actually designed for T12 but T8 still works (with more rapid loss of bulb life).

I'd rather run T8's, but only if the fixture was truly designed for that!

Do some ballasts work well for both T8 and T12?

Thanks!

Ted


I recently opened up a cheap twin Lithonia?? 4ft fixture that claimed to support t12 and t8 lamps and was surprised that the Chinese YC 322516E2 rapid start ballast was rated for almost all the t8 and t12 lamps ever made between 15 and 40W.
I doubt that more than one of the listed lamp pairs could be run efficiently especially as the 34W T12s I use tend to blacken at one end and fail within a year. The fixture is on 24/7.
As I have a number of 4ft T12s set aside I am intend to replace the ballast with a Standard E240T12RS120/N which is rated for 34 or 40W lamps.
My other experience with cheap 4 ft fixtures was a twin T8 unit with a Chinese instant start ballast sold by Canarm which only lasted about a week and failed shorting the supply and tripping the breaker. That unit was replaced with a Mexico made Cooper unit which included a Philips instant start ballast.
Cheap fixtures marketed by Lithonia, Canarm and Lights of America are likely of Chinese origin with cheap ballasts possibly rated for 1000 hours. In the case of Canarm, the steel construction is a lighter gauge with poorly stamped knockouts and inferior lamp sockets. So you do get what you pay for.
 