Fluorescent ballasts

samygero

Newly Enlightened
Joined
Sep 9, 2013
Messages
3
Hello,

My building has quite a few T8 2 lamp fixtures with lamps of 32 Watts. I would like to have an approximation of the peak power that flows through the system on the start-up phase.

Also the ballast is the Advance - GCN2S32TP so it's a series ballast. Does that mean that if one lamp fails or is disconnected the other one will stop working?

Thx for your answers.
 

SemiMan

Banned
Joined
Jan 13, 2005
Messages
3,899
Hello,

My building has quite a few T8 2 lamp fixtures with lamps of 32 Watts. I would like to have an approximation of the peak power that flows through the system on the start-up phase.

Also the ballast is the Advance - GCN2S32TP so it's a series ballast. Does that mean that if one lamp fails or is disconnected the other one will stop working?

Thx for your answers.


I could not find anything on the Inrush current so I will assume it is a standard non inrush controlled unit. That could mean 40-50 amps per unit for a brief period of time while capacitors charge. After that, it will settle down to its average.
 