    Hi guys, I've got a APC UPS of which the battery is not fine anymore. I suppose I can open the device without electrocuting myself using common sense?

    Secondly, while I am replacing the battery, why can't I replace it with a bigger capacity lead acid that can stand next to the UPS? Can it be done without a problem? I am thinking of getting a huge capacity 102A connected to it.

  2. #2
    Flashaholic* Timothybil's Avatar
    Join Date
    Nov 2007
    Location
    The great state of Iowa
    Posts
    3,262

    Default Re: Replacement battery for UPS

    All of the APC UPSs are designed for the user to be able to change the battery. Directions usually come with the replacement battery. AFAIK, it shouldn't be a problem to parallel another battery externally. Just determine what voltage is required before you purchase. I say this because some of the larger UPSs have two batteries in series, some in parallel, and you will want to echo whichever setup yours has. I would strongly recommend a battery case of some sort for the external battery(s), to protect against dirt, moisture, and shorts. Be sure to use heavy enough cables between the two as well. I would go up at least one size larger than the cables on the internal battery, due to the greater distance involved.
    Let us know what you do and how well it turns out. Pictures would be nice.
    Remember, Two is One, and One is None!.

  3. #3

    Default Re: Replacement battery for UPS

    Quote Originally Posted by Timothybil View Post
    All of the APC UPSs are designed for the user to be able to change the battery. Directions usually come with the replacement battery. AFAIK, it shouldn't be a problem to parallel another battery externally. Just determine what voltage is required before you purchase. I say this because some of the larger UPSs have two batteries in series, some in parallel, and you will want to echo whichever setup yours has. I would strongly recommend a battery case of some sort for the external battery(s), to protect against dirt, moisture, and shorts. Be sure to use heavy enough cables between the two as well. I would go up at least one size larger than the cables on the internal battery, due to the greater distance involved.
    Let us know what you do and how well it turns out. Pictures would be nice.
    Thanks.
    If I connect the bigger battery, I will couple it directly to the terminals of the UPS and will not buy the smaller original batteries as well.

  4. #4
    Flashaholic*
    Join Date
    Jan 2014
    Location
    Blue Ridge Mountains, VA
    Posts
    2,328

    Default Re: Replacement battery for UPS

    Quote Originally Posted by lightseeker2009 View Post
    Hi guys, I've got a APC UPS of which the battery is not fine anymore. I suppose I can open the device without electrocuting myself using common sense?

    Secondly, while I am replacing the battery, why can't I replace it with a bigger capacity lead acid that can stand next to the UPS? Can it be done without a problem? I am thinking of getting a huge capacity 102A connected to it.

    Before opening the UPS, unplug the unit and remove the battery isolation plug. This will keep you from getting hit with 120 volts.

    You didn't mention the model number of the unit, it does matter.

    The most common battery for UPS units larger than 1000 vA is the RBC7 pack. The pack is made up of two sealed lead acid 6 volt batteries wired in series with a 40-60 amp fuse or circuit breaker. Provided that your unit uses the standard plug in connection, you can splice the wires to extend them for using another type of battery. A deep cycle automotive/marine battery in a case is going to give you the longest run time. I'd suggest not using a sealed battery, but one that you can check the electrolyte level in. Being on a constant charge, the sealed batteries usually fail by being over charged and splitting the case.

  5. #5

    Default Re: Replacement battery for UPS

    Quote Originally Posted by NoNotAgain View Post
    Before opening the UPS, unplug the unit and remove the battery isolation plug. This will keep you from getting hit with 120 volts.

    You didn't mention the model number of the unit, it does matter.

    The most common battery for UPS units larger than 1000 vA is the RBC7 pack. The pack is made up of two sealed lead acid 6 volt batteries wired in series with a 40-60 amp fuse or circuit breaker. Provided that your unit uses the standard plug in connection, you can splice the wires to extend them for using another type of battery. A deep cycle automotive/marine battery in a case is going to give you the longest run time. I'd suggest not using a sealed battery, but one that you can check the electrolyte level in. Being on a constant charge, the sealed batteries usually fail by being over charged and splitting the case.
    I think you got this wrong... I don't think the RBC7 pack uses 6v batteries but rather 2 x 12v battery in series for 24v as I've taken apart quite a few APC UPSes. In other words the larger UPSes won't run off 1 12v battery at all they require 24v. The UPSes that require only 12v are smaller 600VA or less I believe once you get up to the 1000VA range they go to 24v systems.
    Last edited by Lynx_Arc; 04-26-2015 at 11:02 AM.
    Fenix Split rings 1400+ sent, SWIVELS now available also!
    Psalm 112:4 Light shines in the darkness for the godly. They are generous, compassionate, and righteous.

  6. #6
    Flashaholic*
    Join Date
    Jan 2014
    Location
    Blue Ridge Mountains, VA
    Posts
    2,328

    Default Re: Replacement battery for UPS

    Quote Originally Posted by Lynx_Arc View Post
    I think you got this wrong... I don't think the RBC7 pack uses 6v batteries but rather 2 x 12v battery in series for 24v as I've taken apart quite a few APC UPSes. In other words the larger UPSes won't run off 1 12v battery at all they require 24v. The UPSes that require only 12v are smaller 600VA or less I believe once you get up to the 1000VA range they go to 24v systems.
    Lynx Arc, you're correct on the 12 batteries being used. UPS units under 2200VA (the 1000 and 1500VA units) use a single battery pack that is made up of two 12 volt packs wired in series with a slow blow fuse link between them. The larger units use two battery packs of the same configuration.

  7. #7
    Flashaholic* Timothybil's Avatar
    Join Date
    Nov 2007
    Location
    The great state of Iowa
    Posts
    3,262

    Default Re: Replacement battery for UPS

    How will two larger batteries in series like being recharged that way? I know my 1000vA APC has a reasonably slow recharge rate since it takes 10-12 hours to recharge. Will larger batteries have any problems recharging in series with a low recharge rate? I have been toying with the idea, but just planned on getting two replacement packs and wiring one externally to keep things even.
    Remember, Two is One, and One is None!.

  8. #8

    Default Re: Replacement battery for UPS

    Quote Originally Posted by Timothybil View Post
    How will two larger batteries in series like being recharged that way? I know my 1000vA APC has a reasonably slow recharge rate since it takes 10-12 hours to recharge. Will larger batteries have any problems recharging in series with a low recharge rate? I have been toying with the idea, but just planned on getting two replacement packs and wiring one externally to keep things even.
    From what I could gather what Lynx said. The system might overheat as it was not designed to charge so long at any one time. It was designed to be only working for 5 minutes, now I want to run it 2 hours. Quite a big difference. But then again, I could always supplement the UPS by charging the external battery with another charger.

  9. #9
    Flashaholic*
    Join Date
    Jun 2014
    Location
    Canada
    Posts
    2,823

    Default Re: Replacement battery for UPS

    Quote Originally Posted by lightseeker2009 View Post
    From what I could gather what Lynx said. The system might overheat as it was not designed to charge so long at any one time. It was designed to be only working for 5 minutes, now I want to run it 2 hours. Quite a big difference. But then again, I could always supplement the UPS by charging the external battery with another charger.
    My APC UPS has a fan that kicks in as soon as it takes over. So, I doubt it will overheat from constant use. Perhaps smaller units (without fan) might. I think all the larger APC units have fans (I'm guessing those over 1000VA).

    As for charging a large external battery, I don't think there's a risk of overheating, because the charge rate is so slow. The issue may be that it takes several days to recharge it.

  10. #10
    Flashaholic*
    Join Date
    Jan 2014
    Location
    Blue Ridge Mountains, VA
    Posts
    2,328

    Default Re: Replacement battery for UPS

    If you get to the point when you have had to use the unit as back up power, I'd unplug the batteries and charge them with another charger before reconnection. Your advantage will be that the batteries will be readily accessible.

  11. #11

    Default Re: Replacement battery for UPS

    Other thing is, I can't think the 102A will even come down to 50% charge after two hours, so it is not as if the battery will have zero charge left. That should help a bit.

  12. #12

    Default Re: Replacement battery for UPS

    Quote Originally Posted by lightseeker2009 View Post
    Other thing is, I can't think the 102A will even come down to 50% charge after two hours, so it is not as if the battery will have zero charge left. That should help a bit.
    Without a good idea what load you will have on it I wouldn't know for sure. Inverters aren't 100% efficient perhaps 85% efficient and a 102Ah battery won't deliver that total when the current load starts rising beyond a certain point. If the battery is deep cycle the rating is for about 5A draw per hour exceeding that amount drops your 102Ah number down considerably with increasing current draw. At a 20A draw on the battery the capacity can drop down about 20 to 50% from rated and the inverter would only be delivering around 2A at 120v to your stuff.
    Last edited by Lynx_Arc; 04-26-2015 at 02:44 PM.
    Fenix Split rings 1400+ sent, SWIVELS now available also!
    Psalm 112:4 Light shines in the darkness for the godly. They are generous, compassionate, and righteous.

  13. #13

    Default Re: Replacement battery for UPS

    Quote Originally Posted by Lynx_Arc View Post
    Without a good idea what load you will have on it I wouldn't know for sure. Inverters aren't 100% efficient perhaps 85% efficient and a 102Ah battery won't deliver that total when the current load starts rising beyond a certain point. If the battery is deep cycle the rating is for about 5A draw per hour exceeding that amount drops your 102Ah number down considerably with increasing current draw. At a 20A draw on the battery the capacity can drop down about 20 to 50% from rated and the inverter would only be delivering around 2A at 120v to your stuff.
    I will power only my 40'' LED tv and my decoder. We are on 220V. For lights, I don't need them, I have tons of flashlights

  14. #14
    Flashaholic
    Join Date
    Nov 2007
    Location
    Somerset UK
    Posts
    394

    Default Re: Replacement battery for UPS

    Yes you can connect a large external battery to a UPS in place of the small internal battery, I have done this several times.
    Since the larger battery will permit of a much longer run time, I would be concerned that the inverter might overheat. For this reason I would limit the load to about 50 % of the rating.
    The built in battery charger will indeed take longer to charge the much larger battery, I would simply accept this. I doubt that the battery charger will overheat since it is designed to run for some hours. I doubt that the charging circuit will get any hotter after 24 hours than after the say 6 hours to charge the internal battery.

    The most important point to be aware of is that the internal battery may NOT BE ISOLATED FROM THE LINE SUPPLY and therefore perhaps fatal line voltage electric shock could be received from the battery terminals. It is therefore MOST IMPORTANT that the battery terminals be treated with the same respect as line voltage connections.
    I would place the battery in a strong plastic crate with lid secured.

    UL, CE or other safety listing sets strict standards for the isolation between line voltage and connections that can be touched by the user. These standards DO NOT apply to UPS units as the batteries are intended to be internal and not able to be touched.

  15. #15

    Default Re: Replacement battery for UPS

    @ Broadgage. Can it really be that the battery terminals can go over 12/24V? That would surely fry the batteries? I thought I will never risk a shock by just touching the leads from the lead acid.

  16. #16
    Flashaholic*
    Join Date
    Jan 2014
    Location
    Blue Ridge Mountains, VA
    Posts
    2,328

    Default Re: Replacement battery for UPS

    lightseeker,

    If you are using the APC branded UPS, go to APC's website and download the manual for your unit. You'll need the model number and possibly the serial number.

    Ensure that the unit isn't plugged into supply voltage, which you stated earlier was 220 volts. Wire the external batteries in series, and use the APC blade connector to connect the batteries to the UPS. Once the batteries are connected, turn the unit on and let it perform the self check. Then apply a load to the unit and verify that the load indicator lights work. A hand held hair dryer should supply enough current draw to show if the unit is working correctly.

  17. #17

    Default Re: Replacement battery for UPS

    Guys, I was wrong about the brand. Its not a APC. My friend who gave it to me said its a APC.
    The model number of the UPS I have is: BNT-1000AP. I am so sorry for this, I never used it before as it is a gift after the battery died.
    It is a 600W, 1000VA UPS . My TV and decoder will use less than 50% of the current this UPS can deliver.
    There is not much I can find on the internet about this UPS, mostly in languages I don't understand. Sorry for not making sure before I posted. I am going to take it apart now, that is when I realized it is not a APC.

  18. #18
    Flashaholic* Timothybil's Avatar
    Join Date
    Nov 2007
    Location
    The great state of Iowa
    Posts
    3,262

    Default Re: Replacement battery for UPS

    When I googled the part number, I found a page of illustrations that included the batteries. It appears it uses four 12v, 8or9Ah batteries in a series parallel arrangement, for a total of 24v & 16/18Ahs, or around 400WH. The UB 1280 battery shown is an AGM SLA with nut and bolt terminals. The next step up to the size you are talking about would be the 35/55 AH batteries, at about $120 + shipping each.
    Remember, Two is One, and One is None!.

  19. #19
    Flashaholic
    Join Date
    Nov 2007
    Location
    Somerset UK
    Posts
    394

    Default Re: Replacement battery for UPS

    Quote Originally Posted by lightseeker2009 View Post
    @ Broadgage. Can it really be that the battery terminals can go over 12/24V? That would surely fry the batteries? I thought I will never risk a shock by just touching the leads from the lead acid.
    I am not suggesting that the battery is directly connected across the line voltage input, that would indeed fry the battery as the line supply is both AC and the wrong voltage.
    What is entirely possible though is for one side of the battery to be connected to one side of the line supply, the battery would still receive the correct DC charging voltage, but would ALSO be live at line voltage and therefore dangerous to touch.

    Battery chargers sold for charging vehicle batteries etc have the output carefully isolated from the line voltage input to avoid danger if the battery or connecting clips be touched in use. This is a legal requirement in all developed countries.
    Battery chargers built into UPS units do not have to comply with this requirement because the battery is intended to be enclosed within the equipment and not accessible to touch.

  20. #20
    Flashaholic*
    Join Date
    Jan 2014
    Location
    Blue Ridge Mountains, VA
    Posts
    2,328

    Default Re: Replacement battery for UPS

    Quote Originally Posted by lightseeker2009 View Post
    Guys, I was wrong about the brand. Its not a APC. My friend who gave it to me said its a APC.
    The model number of the UPS I have is: BNT-1000AP. I am so sorry for this, I never used it before as it is a gift after the battery died.
    It is a 600W, 1000VA UPS . My TV and decoder will use less than 50% of the current this UPS can deliver.
    There is not much I can find on the internet about this UPS, mostly in languages I don't understand. Sorry for not making sure before I posted. I am going to take it apart now, that is when I realized it is not a APC.
    A Google search of the part number supplied led me to this http://www.powercom-usa.com/ProductDetail.asp?ID=8974 If it were me, I'd send them an email for any technical info (user manuals) as well as a schematic for the unit.

  21. #21
    Flashaholic*
    Join Date
    Mar 2007
    Location
    Brisbane, Australia
    Posts
    634

    Default Re: Replacement battery for UPS

    Quote Originally Posted by broadgage View Post
    Battery chargers built into UPS units do not have to comply with this requirement because the battery is intended to be enclosed within the equipment and not accessible to touch.
    That may be true in general, but as far as I recall, the APC units are designed for the end user to be able to replace the battery - while the unit is still connected to the mains and supplying power to the load. I'd be very surprised if the battery terminals in the APC units weren't well isolated from the mains.

    Obviously, the unit isn't going to act as a UPS whilst there are no batteries connected, but it does save having to power down the load to be able to swap out the batteries.
    Firmware Developer for the UltraSmartCharger: Open Source Charger/Analyzer for NiMH/NiCad/NiZn batteries.
    http://www.ultrasmartcharger.com

  22. #22
    Flashaholic* Timothybil's Avatar
    Join Date
    Nov 2007
    Location
    The great state of Iowa
    Posts
    3,262

    Default Re: Replacement battery for UPS

    Quote Originally Posted by broadgage View Post
    I am not suggesting that the battery is directly connected across the line voltage input, that would indeed fry the battery as the line supply is both AC and the wrong voltage.
    What is entirely possible though is for one side of the battery to be connected to one side of the line supply, the battery would still receive the correct DC charging voltage, but would ALSO be live at line voltage and therefore dangerous to touch.

    Battery chargers sold for charging vehicle batteries etc have the output carefully isolated from the line voltage input to avoid danger if the battery or connecting clips be touched in use. This is a legal requirement in all developed countries.
    Battery chargers built into UPS units do not have to comply with this requirement because the battery is intended to be enclosed within the equipment and not accessible to touch.
    I agree that in cheaper equipment it is entirely possible that one terminal on the battery could be connected to the Chassis GROUND, which in turn would be connected to Earth GROUND through the main panel, and to Earth GROUND directly through the third wire system GROUND pin. Any UPC that does not have a three-wire cord and plug to connect to a GROUNDed outlet is not safe and should not be used. It is the same rational as polarized plugs on lamps, radios, clocks, etc. It helps to ensure that any area where a user may be exposed to live contacts will be touching the ground side of the line, and not the hot.
    Remember, Two is One, and One is None!.

  23. #23

    Default Re: Replacement battery for UPS

    One side of battery is connected to live mains, so always unplug and take care when handling.
    In most APC UPS's (at least relatively older models) charging is controlled via LM2577 IC, and since it has short current/overload protection, larger battery won't be a problem when charging, but it should be noted that UPS inverter is might not be rated for longer runtimes, so you have to add additional cooling, or use it at 1/10 power rating or smaller. Personally, I've connected PowerCom BNT-600A UPS to car 12V 65Ah battery, and it works like charm for last 5 years. It should be noted that I'm loading it very lightly - back ups my torrent box and router.

  24. #24

    Default Re: Replacement battery for UPS

    Is it safe to use a car battery indoors? Don't they give off gasses while charging?

  25. #25

    Default Re: Replacement battery for UPS

    Mine is located on balcony.

    Also, a lot of APC Smart UPS series have "turn off timer", which needed to be turned off via service software.

  26. #26

    Default Re: Replacement battery for UPS

    Quote Originally Posted by Timothybil View Post
    When I googled the part number, I found a page of illustrations that included the batteries. It appears it uses four 12v, 8or9Ah batteries in a series parallel arrangement, for a total of 24v & 16/18Ahs, or around 400WH. The UB 1280 battery shown is an AGM SLA with nut and bolt terminals. The next step up to the size you are talking about would be the 35/55 AH batteries, at about $120 + shipping each.

    Bahhhhh.

    Ebay.

    Every 3 years I buy 3 sets of batteries for the UPSs from typically the cheapest vendors (to the US). They've run just fine.

    Just a thought- I think I pay about 40$? (can't get to ebay from work)

  27. #27

    Default Re: Replacement battery for UPS

    Quote Originally Posted by lightseeker2009 View Post
    Is it safe to use a car battery indoors? Don't they give off gasses while charging?
    Yes, they do, and they have to be maintained with water.

    Also they have a different charging profile than most batteries in UPS (wet, SLA, AGM). You *can* get away with a deep cycle marine and changing the top off voltage if the unit allows you to, but...

  28. #28
    Flashaholic* Timothybil's Avatar
    Join Date
    Nov 2007
    Location
    The great state of Iowa
    Posts
    3,262

    Default Re: Replacement battery for UPS

    Quote Originally Posted by purduephotog View Post
    Bahhhhh.

    Ebay.

    Every 3 years I buy 3 sets of batteries for the UPSs from typically the cheapest vendors (to the US). They've run just fine.

    Just a thought- I think I pay about 40$? (can't get to ebay from work)
    If you are buying UPS batteries, you are not buying 35/55AH batteries, either. Even if you could get them for half price, they would still be over $50 each + shipping.
    Remember, Two is One, and One is None!.

  29. #29
    Flashaholic
    Join Date
    Nov 2007
    Location
    Somerset UK
    Posts
    394

    Default Re: Replacement battery for UPS

    Quote Originally Posted by lightseeker2009 View Post
    Is it safe to use a car battery indoors? Don't they give off gasses while charging?
    Yes, with a bit of common sense it is safe to use a car or similar battery indoors. Provided that significant over charging is avoided by use of a fully automatic battery charger then the amount of gas evolved is harmless in a normal size room except very close to the battery.
    It would be well not to smoke or allow a naked flame close to the battery, but in the same room should be fine.

    Many disabled people use powered wheelchairs, these are normally used, stored and charged indoors without this being considered dangerous. Until very recently electric wheelchairs used vented lead acid batteries, and some probably still do.
    Many domestic garages are used as stores workshops or utility rooms and no one worries about the battery in the car.

  30. #30
    Flashaholic*
    Join Date
    Jan 2014
    Location
    Blue Ridge Mountains, VA
    Posts
    2,328

    Default Re: Replacement battery for UPS

    IMO, the only time that charging a wet acid battery indoors would present a danger is if you are rapidly charging the battery. Rapid charging generates higher quantities of hydrogen gas. A slow, 1-2 amp charge rate emits minimal gas. Hard charging where you bring the sulfuric acid to a boiling point is where the maximum gas is generated.