My home A/C is not working, the line going into my furnace are freezing up.. Solid ice.
Extensive research shows me this could indicate two problems, low freon or restricted airflow. When I run my furnace fan without air or heat I am certainly not getting the same airflow I typically do. I have a brand new air filter, all vents are open and I still don't seem to be passing much air through the furnace.. The fan is running strong and their are no visible blockages inside the furnace either..
I just don't get it..
One more day of 90 degree heat is all I can take..
I have never hired a contractor for anything, and I would hate to break down for something that seems so simple..
 

raggie33

*the raggedier*
Joined
Aug 11, 2003
Messages
13,547
im in same boat o im so about to lose my mind i hate the heat py .i can sleep when its 30f in my room no probs but i cant handle heat im about to sell my pc and rent a hotel for a few days i rather live ina a 10x10 room and have ac then in this house with out it.btw it sound slike low air flow to me to try to replace ac filter then check to see if coil is clean the evaprater coil which is the one in furnace usaly or air handler
 

snakebite

Flashlight Enthusiast
Joined
Mar 17, 2001
Messages
2,725
Location
dayton oh
sounds like a filthy A coil.
this could be easy to clean or an all day job tearing the whole thing apart to get access to it.
most common cause is running without a filter.
 

Pydpiper

Flashlight Enthusiast
Joined
Jan 4, 2005
Messages
1,778
Location
Brantford/Woodstock
The coils inside the furnace appear to be clean, to my eyes anyways.. I can see the odd dog hair on it though. Is the dirt build up something I would be able to see or not?
I can see the coils inside the furnace, i can gt at them enought to clean them, is that difficult? Mix a homebrew solution or is their a product that will yeild better results?
I sure do get miserable when it's hot..
 

raggie33

*the raggedier*
Joined
Aug 11, 2003
Messages
13,547
man i nerer thought it got cold in canada man they should give ya a break after the winter there .canada has hot women though lol
 

Lynx_Arc

Flashaholic
Joined
Oct 1, 2004
Messages
11,212
Location
Tulsa,OK
sounds like low freon to me, the coils have to be very filthy to freeze up a system... essentially almost completely blocking air flow.
 

powernoodle

Flashlight Enthusiast
Joined
Feb 25, 2004
Messages
2,512
Location
secret underground bunker
Pydpiper said:
When I run my furnace fan without air or heat I am certainly not getting the same airflow I typically do.

That makes it sound like the blower/fan is the problem. Low coolant (its probably not freon) won't cause a reduction in air flow. It will just make the air flow less cool. Plus, low coolant likely will cause the coil to turn into a solid chunk of ice that you would see if you are looking at the coil. By coil I mean the flat panel or A-frame shaped panel that cools off the air as the air passes over it.

So my vote is for a blower/fan problem. You could still have low coolant, but like I say that wont reduce the volume of air that gets moved. JMO.

cheers
 

Pydpiper

Flashlight Enthusiast
Joined
Jan 4, 2005
Messages
1,778
Location
Brantford/Woodstock
OK..
After applying my mechanical engineering skills I realized that I was looking at the wrong side of the coils, it was the inside of the "A" I should have been looking at.. :whistle:
That is the last time I order a diploma from the internet. :)
So, after some brute force and a little cleaning I removed the thick layer of "stuff" from the inside of the "A" Coil, 70 degrees and dropping, airflow is restored..
Thanks guys, my family thanks you as well. :)

Raggie, don't let the country's name fool you, I live farther south than a good chunk of the US..
 

zespectre

Flashlight Enthusiast
Joined
May 21, 2005
Messages
2,197
Location
Lost in NY
Now make sure you also get a good filter in place on that system!

Glad you're cooling down. We snapped from cool/damp to HOT/humid in ONE DAY here. That kind of a transition is pretty rough to take.
 

cy

Flashaholic
Joined
Dec 20, 2003
Messages
8,186
Location
USA
glad you figured it out.... clogged A-frame coil is a common issue.

superheat and subcooling are two terms one needs to know to truly understand refrigeration.
 

ChocolateLab33

Flashlight Enthusiast
Joined
Apr 22, 2004
Messages
1,276
Location
Sarasota, FL
Not that this helps or matters or anything........but I just had to have my coil replaced on my furnace. It was leaking freon very bad. $650 to replace. OUCH. But I can't live without A/C.
spoiled:sssh:
 