    Default Post-mortem report on significant Li-ion incident

    I came across this very detailed / exhaustive report that was recently released following the analysis of a rather significant Li-ion battery system event which occurred at a power utility storage installation here in AZ last year. I didn't read the entire report verbatim, but scanned through it and found some sections of information which I found very interesting. While perhaps 'too much information' for some, some might like to scan through it for sections which might be of interest.....or not. Suffice it to say that when this stuff goes wrong, it can go wrong in a big way (which in itself is of course is not 'news' to most of us). The report also includes some references to / information regarding several other significant 'incidents' which made the news in the past.

    https://www.aps.com/-/media/APS/APSC...D276C40FA54FCE

    - Richard

  2. #2
    Flashaholic* turbodog's Avatar
    Join Date
    Jun 2003
    Location
    Southern USA
    Posts
    4,669

    Default Re: Post-mortem report on significant Li-ion incident

    Thorough report. Did the firemen get hurt? If it said this I missed it.

    Nothing new in the report. Dendrites, internal short, thermal runaway, cascading to adjacent cells, flammable gas buildup, explosion.

    Someone familiar with enough cross-discipline info could have prevented this during design phase. Failures all across the board... including the fire crew that opened the door.
    This is your life, and it's ending one minute at a time.
    Be prepared for the truth.

  3. #3
    *Flashaholic* idleprocess's Avatar
    Join Date
    Feb 2004
    Location
    dfw.tx.us
    Posts
    5,522

    Default Re: Post-mortem report on significant Li-ion incident

    It's incidents like this that have stopped me from DIY'ing large powerbanks or powerwalls - more or less none of the builds I've seen seem to account for these contingencies outside of attempting to contain a fire ala siting them separate from a residence or using a metal container for the cells.
    I apologize that this letter is so long; I did not have time to write a short letter

  4. #4
    Flashaholic Katherine Alicia's Avatar
    Join Date
    May 2020
    Location
    Central UK.
    Posts
    232

    Default Re: Post-mortem report on significant Li-ion incident

    I`v ofen thought about this if I were to design another large Li Ion based power bank again, and I think I`d probably have them spring loaded as one of the connections and soldered using Wood`s metal to the bus bar for the other rail, so if any one cell ever overheated (above 70c) it would automatically be ejected from the bank by the spring because the wood`s metal holding it in place would have melted.
    There are Other alloys that can be used as well for a variety of different temperatures.
    but that`s as far as I got in my design, I`m sure smarter folks than me could make it work though.

  5. #5
    KITROBASKIN's Avatar
    Join Date
    Mar 2013
    Location
    New Mexico, USA
    Posts
    3,245

    Default Re: Post-mortem report on significant Li-ion incident

    From the report:

    At approximately 16:54 on April 19, 2019, a battery cell in Module 2 of Rack 15 of the BESS experienced asudden drop in voltage during a charge cycle, equivalent to a single cell voltage drop (4.06 to 3.82 V asshown in Figure 14). Module 2 was in the second module position, numbered upward from the base of therack.Moments after the voltage drop occurred, cell 7 in module 2 of rack 15 went into thermal runaway. Thisevent generated off-gassing and smoke that activated the VESDA smoke detection system and led to thedischarge of the Novec 1230 agent. The initiating cellís thermal runaway cascaded into thermal runaway ofneighboring cells within module 2 and subsequently into the batteries contained within neighboring modules.The off-gassing of battery cells from the cascading thermal runaway created a flammable atmosphere withinthe BESS.Approximately 3 hours after the initial voltage drop and discharge of the fire suppressant, firefightersopened the side container door, and approximately 2-3 minutes after the door was opened, an explosionoccurred. The doors on the side and rear of the BESS and other debris were ejected by the explosion asshown in the figures below. At approximately 16:54 on April 19, 2019, a battery cell in Module 2 of Rack 15 of the BESS experienced asudden drop in voltage during a charge cycle, equivalent to a single cell voltage drop (4.06 to 3.82 V asshown in Figure 14). Module 2 was in the second module position, numbered upward from the base of therack.Moments after the voltage drop occurred, cell 7 in module 2 of rack 15 went into thermal runaway. Thisevent generated off-gassing and smoke that activated the VESDA smoke detection system and led to thedischarge of the Novec 1230 agent. The initiating cellís thermal runaway cascaded into thermal runaway ofneighboring cells within module 2 and subsequently into the batteries contained within neighboring modules.The off-gassing of battery cells from the cascading thermal runaway created a flammable atmosphere withinthe BESS.Approximately 3 hours after the initial voltage drop and discharge of the fire suppressant, firefightersopened the side container door, and approximately 2-3 minutes after the door was opened, an explosionoccurred. The doors on the side and rear of the BESS and other debris were ejected by the explosion asshown in the figures below.

  6. #6
    Flashaholic* turbodog's Avatar
    Join Date
    Jun 2003
    Location
    Southern USA
    Posts
    4,669

    Default Re: Post-mortem report on significant Li-ion incident

    Quote Originally Posted by idleprocess View Post
    It's incidents like this that have stopped me from DIY'ing large powerbanks or powerwalls - more or less none of the builds I've seen seem to account for these contingencies outside of attempting to contain a fire ala siting them separate from a residence or using a metal container for the cells.
    You could put the pack in a standard jobsite toolbox, clamp the lid thoroughly, and put some vents in to allow gases to escape.

    But yeah... still would not sleep well. I am paranoid with the lipo packs for r/c that I have.
    This is your life, and it's ending one minute at a time.
    Be prepared for the truth.

  7. #7
    *Flashaholic* idleprocess's Avatar
    Join Date
    Feb 2004
    Location
    dfw.tx.us
    Posts
    5,522

    Default Re: Post-mortem report on significant Li-ion incident

    Quote Originally Posted by turbodog View Post
    You could put the pack in a standard jobsite toolbox, clamp the lid thoroughly, and put some vents in to allow gases to escape.

    But yeah... still would not sleep well. I am paranoid with the lipo packs for r/c that I have.
    For a DIY powerwall, I've considered just burying the thing. If the cells can sink their heat to the earth and the enclosure has some means of venting to atmosphere, seems like any destructive fires could be safely contained under 12-18" of soil so long as it's otherwise well-sealed.
    Last edited by idleprocess; 08-13-2020 at 06:57 PM.
    I apologize that this letter is so long; I did not have time to write a short letter

  8. #8

    Default Re: Post-mortem report on significant Li-ion incident

    Iíd say I have a healthy fear of lithium ion batteries. Ainít no way Iím buying an electric car until they figure out an alternative, like those supposed holy grail quantum glass cells. I barely tolerate laptop-size cells as it is.

    Donít even get me started on internet order E-bicycles. People are buying time bombs and storing them either inside inhabited homes or next to cars and flammable garage items, never mind how awful they are to deal with as a bike mechanic.
    Streamlight ProTac HL - SureFire P2X Fury - Fenix PD35 v2.0 - Lumintop Tool AA 2.0 - Fenix PD25 - Sunwayman V11R XML2 6A3 mod - Olight Warrior X Pro

  9. #9

    Default Re: Post-mortem report on significant Li-ion incident

    Yes, numerous firemen were hurt. They are alive because of the turnout gear they were wearing and the fact that the fence around the facility was chain link. It allowed the force of the explosion to dissipate over a greater area, vs a bock wall. And they were blown under the fence, vs being pinned against a block wall. Most of them have recovered from their injuries, one is still recovering and not back to full duty. Iím not with the fire department, but work closely with them.

  10. #10
    KITROBASKIN's Avatar
    Join Date
    Mar 2013
    Location
    New Mexico, USA
    Posts
    3,245

    Default Re: Post-mortem report on significant Li-ion incident

    Great to hear that update, mr45acp2u.