just some data on power lines for your rumination.
In case you don't think that you need a UPS......
A common feeder from a power station is 13800VAC 3 phase @ 4000-5000Amps in a Y configuration. If a phase fault occurs, a common high-voltage vacuum breaker will break the circuit w/in 10-15 cycles. It takes about 5 cycles for the breaker to stabilize after opening. The average breaker is set to reclose in 5 seconds or so. That constitutes the two "bang.....bang" hits that happen when a main feeder goes out. Spectacular if you should happen to be anywhere close - hopefully not! If the line is still in fault, the breaker reopens and stays open. Human intervention is then required.
Another note about feeder faults. If one phase shorts to ground, the next close of the breaker will usually find another phase shorted to ground. Suffice to say that with currents of the magnitude that will flow to ground during a short-circuit condition on a feeder line will cause signficant neutral and ground currents to flow. At that voltage, the ground is a nice high-wattage resistor. I will let you do the multiplication..... The end result is that both the neutral and the ground in the area will NOT be at zero volts. What that voltage could be is dependent on how close your sensitive equipment is to the fault or the power station. A mile or two at those voltages and currents is not much protection if the current should happen to flow on the surface of the ground!
As for the typical UPS, I happen to have the APC Backup UPS ES 750 with tel and coax protection. equivalent to 450watts. The transfer time to battery in a failure is listed as 6 milliseconds typical and 10 milliseconds maximum. In general, the company I work for has good experiences with the APC units in comm closets. Besides my own unit, I installed APC UPS units at a couple churches - no call backs at all, and yes, they are in use.
There are other good UPSs, but as was pointed out above, pay attention to the noise reduction, not just the spike/surge protection!
Tim