From the report:
At approximately 16:54 on April 19, 2019, a battery cell in Module 2 of Rack 15 of the BESS experienced asudden drop in voltage during a charge cycle, equivalent to a single cell voltage drop (4.06 to 3.82 V asshown in Figure 14). Module 2 was in the second module position, numbered upward from the base of therack.Moments after the voltage drop occurred, cell 7 in module 2 of rack 15 went into thermal runaway. Thisevent generated off-gassing and smoke that activated the VESDA smoke detection system and led to thedischarge of the Novec 1230 agent. The initiating cell's thermal runaway cascaded into thermal runaway ofneighboring cells within module 2 and subsequently into the batteries contained within neighboring modules.The off-gassing of battery cells from the cascading thermal runaway created a flammable atmosphere withinthe BESS.Approximately 3 hours after the initial voltage drop and discharge of the fire suppressant, firefightersopened the side container door, and approximately 2-3 minutes after the door was opened, an explosionoccurred. The doors on the side and rear of the BESS and other debris were ejected by the explosion asshown in the figures below. At approximately 16:54 on April 19, 2019, a battery cell in Module 2 of Rack 15 of the BESS experienced asudden drop in voltage during a charge cycle, equivalent to a single cell voltage drop (4.06 to 3.82 V asshown in Figure 14). Module 2 was in the second module position, numbered upward from the base of therack.Moments after the voltage drop occurred, cell 7 in module 2 of rack 15 went into thermal runaway. Thisevent generated off-gassing and smoke that activated the VESDA smoke detection system and led to thedischarge of the Novec 1230 agent. The initiating cell's thermal runaway cascaded into thermal runaway ofneighboring cells within module 2 and subsequently into the batteries contained within neighboring modules.The off-gassing of battery cells from the cascading thermal runaway created a flammable atmosphere withinthe BESS.Approximately 3 hours after the initial voltage drop and discharge of the fire suppressant, firefightersopened the side container door, and approximately 2-3 minutes after the door was opened, an explosionoccurred. The doors on the side and rear of the BESS and other debris were ejected by the explosion asshown in the figures below.