This is only tangentially related to fixed lighting, but I thought it was worth running by the CPF brain trust.
I've been having an intermittent problem for several months at home with lights flickering and UPS devices switching over and over between battery and line power. I started probing outlets and breakers with a multimeter and found that one leg of the power service coming from the meter into the panel sometimes drops 8-10V, measuring 110-112V. The other leg is at 118-120V all the time.
Here are my observations:
1. Flickering lights and low voltage at outlets on one phase but not the other. Affected outlets measure 110-112V.
2. Low voltage as measured between the bus bar and hot on every other breaker in the panel.
3. Low voltage on one leg of the mains coming in the top of the panel. The affected leg measures low with or without the main (200A) breaker switched on.
4. Power company pulled the meter and ran a load test at the meter connection and detected a low leg.
Here's what has been done:
1. Electrician rewired two multi-wire branch circuits that were wired incorrectly with both hots on the same phase. This did not fix the issue.
2. After pulling the meter and running a load test (#4 above), the power company replaced ~175 ft. of wire from the pole to the house. This did not fix the issue.
So my questions are:
1. Would you agree this is an issue with the power company's equipment? I don't see how it could be a problem with my home wiring considering observation #3 above.
2. Any idea what kind of equipment failure might cause this? Typical of a transformer on the fritz, or something else?
I've been having an intermittent problem for several months at home with lights flickering and UPS devices switching over and over between battery and line power. I started probing outlets and breakers with a multimeter and found that one leg of the power service coming from the meter into the panel sometimes drops 8-10V, measuring 110-112V. The other leg is at 118-120V all the time.
Here are my observations:
1. Flickering lights and low voltage at outlets on one phase but not the other. Affected outlets measure 110-112V.
2. Low voltage as measured between the bus bar and hot on every other breaker in the panel.
3. Low voltage on one leg of the mains coming in the top of the panel. The affected leg measures low with or without the main (200A) breaker switched on.
4. Power company pulled the meter and ran a load test at the meter connection and detected a low leg.
Here's what has been done:
1. Electrician rewired two multi-wire branch circuits that were wired incorrectly with both hots on the same phase. This did not fix the issue.
2. After pulling the meter and running a load test (#4 above), the power company replaced ~175 ft. of wire from the pole to the house. This did not fix the issue.
So my questions are:
1. Would you agree this is an issue with the power company's equipment? I don't see how it could be a problem with my home wiring considering observation #3 above.
2. Any idea what kind of equipment failure might cause this? Typical of a transformer on the fritz, or something else?