idleprocess
Can't speak to 3-phase power, but I've got a layman's understanding of residential split-phase (read: 2-phase) power. Split phase is something generally unique to North America. With three wires one can produce two 120V phases or a single 240 phase - this works because the two 120V phases are 180° out of phase. Here's an illustration of the common 14-50 120V/240V outlet:Could a 240 Volt construction type generator power some of the pumps? I don't have an understanding of 2 and 3 phase power.
![Uo3vq62.png](https://i.imgur.com/Uo3vq62.png)
- X-N: 120V
- Y-N: 120V
- X-Y: 240V
There's not really a neutral for 240V split-phase, but since there is a 240V delta between the two phases it's effectively the same for loads. A neutral wire is run as a matter of course since 120V control electronics are stupid commonplace.
The closely-related 14-20, 14-30, 14-50 outlets common on 120V/240V portable generators can supply either voltage right out of the box and doesn't care how you draw from it until you overload the rating. You can buy cables that passively convert to common 120V 5-15/5-20 receptacles.
Anyway, as I believe you're already familiar, the busbars on breaker panels are neatly divided into alternating phases - a singlewide breaker is 120V to neutral while a doublewide breaker is 240V between poles.